You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 4616 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 10 posts

Tuesday, September 6th 2011, 8:32pm

by blackhorse16a

Yup, it was the rain detector! Disconnected the wires, all OK.

Thanks for all the help.

Saturday, September 3rd 2011, 9:20am

by Wet_Boots

Also look for a faulty rain detector.

Friday, September 2nd 2011, 3:37pm

by Central Irrigation

You are looking only for a broken Common wire. It should be broken between the controller and the first valve box on it's path. Usual culprits are bad wire connections at the valve itself and areas where recent digging occurred. If none of these seem to be the case, then a wire locator and ground fault locator may need to be used.

Friday, September 2nd 2011, 3:07pm

by blackhorse16a

Yep, infinite Ω on all four zones. BTW, why is there one more wire than the number of zone valves?

Now do I have to dig up the wire?

Friday, September 2nd 2011, 11:40am

by Wet_Boots

Check the resistance of individual zones (controller is off) with one lead on the common wire and one lead on a zone wire. That gives you a measurement that includes the wire out and back. Faulty wiring will show up as infinite resistance, in the case of a break or a bad splice, as will an open circuit in the solenoid itself.

Friday, September 2nd 2011, 10:20am

by blackhorse16a

How do I do this when the controller is far from the valves? E.g., to check the continuity of the common (my prime suspect) do I need a long wire or what?

Thursday, September 1st 2011, 6:22pm

by Wet_Boots

Sure. Try taking some resistance measurements of your zone wiring

Thursday, September 1st 2011, 10:06am

by blackhorse16a

Don't have a spare. Can't I do this with a meter?

Wednesday, August 31st 2011, 9:26pm

by mike1059

testing zones

the next thing to try is seeing if you are getting signal both at the clock and the valves. If you have a spare solenoid touch the wires to the common terminal and each zone terminal as each zone starts and you should here the solenoid click if you have signal then try the same thing at each valve. If you have signal at both spots the solenoids are probably bad but if you only get signal at the clock the common wire probably has a break somewhere.

Wednesday, August 31st 2011, 1:39pm

by blackhorse16a

No Power to Valves

I have a Hunter SRC Plus system with four zones. I cannot run any zones from the controller, auto or manually, since hurricane Irene (we didn't get hit hard here in eastern massachusetts). I opened each zone valve manually at the valve; they work fine. The controller also appears to be fine, display, etc., but I reset it anyway. System still won't run. I assume the transformer's ok, since it runs the controller (no 9v battery is installed).

Where do I go next?

Thanks,

BH