Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.
Attention: The last reply to this post was 4498 days ago. The thread may already be out of date. Please consider creating a new thread.
The last 10 posts
Sprinkler zone starts, but then quits
I'm suspect of valve #1 and the Master Valve....
The first two solenoids' resistances were kinda low, and I didn't see were the master valve was tested for resistance.
I've had solenoids read well within their limits (for any given manufacturer) start shorting out after a period of time [from 10 seconds to as much as 3-5 minutes] - and the longer the solenoid had power, the less the resistance became finally breaking the circuit...
As a soleonid begins to short out the windings, the resistance becomes less and they start to heat up... and the more they heat up, the more windings become shorted...ad infinitum.
Way to check.... Jot down the resistances on all the valves including the master valve. Run the valves in queston and check 'em out right after the clock craps out... is the resistance is lower than it was when you checked it cold? 20 Ohms or less... replace the solenoid....
Good Luck.... Bill
tismaz.com
What's a toner? And that common wire - a ground? I thought it was a neutral.
Yeah Mrfixit, and I did. However, I was only taking resistance readings and the readings weren't necessary out of specs. That's why I used a toner. Thanks though for the help.
Isn't that what someone suggested you try in the very first reply of this post?
Good thing you had a spare wire
Problem solved. I retook resistance readings on all 7 wires in the cable. My common cable was reading pretty low and didn't get any tone on the continuty test, but the other 6 wires were good. So, I swapped it, rewired my valves and everything worked fine. If not, this would have sucked because when they ran he cable they didn't run it through PVC, so pulling the cable would have been impossible unless I tore up the concrete. Again, thanks everyone for your help.
Dave
Hopefully you can atatch new cable to old and pull it under the concrete.
Ok, all. I definetly have a wiring problem. I ran the extension cord to the sprinkler valves and hooked both controllers (old and new) on station. I then connected each station to the control, elminating the main cable. Everything worked perfectly. So, the good news is I can take back the new controller. My next task is to test each lead on the cable. Hopefully, I have a couple good ones. It will be suck to rerun that cable since it is under brand new concrete. FML
I'm located in San Diego. Here is my plan today. I'm going to recheck all voltage and resistance readings. However, my first step is to elminate the wiring portion. I'm going to run an extension cord to the valves and hook each solenoid to the controller, elminating the wiring. This should tell me if I have a problem with the wiring.
That being said, I had a pool installed a couple of months ago and I know the hit the wiring. Everything was fixed (spliced), and has worked fine every since. I have already checked the wiring. Yesterday, I took readings of each wire to ground and read OL. I then shorted on side of the wire and took readings and read a short. So, that shows me the wiring is good. I will start over and do this again. I will let you know what I find today. Thanks