Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 6122 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 8 posts

Wednesday, August 8th 2007, 12:56pm

by mrfixit

They do function well under high pressure. They do close slowly as advertized. I can't promise it will completly cure the problem but it might. I'd say 75% of the systems I've converted to the 800 series were completly cured. The other 25% there was definite decrease in water hammer. I do live in a city where the pressure varies from 50 pounds to 130 depending on location. I suggest you tighten down the screws around the valve. Your high pressure will cause them to leak in a few years if you don't. Good luck!

Wednesday, August 8th 2007, 12:05pm

by BobD

<blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by mrfixit</i>
<br />After reading this article again, I'm thinking that's where I got the above idea from. I guess this is how senility starts. =) The article has some interesting solutions. --
http://www.irrigationtutorials.com/waterhammer.htm
<hr height="1" noshade id="quote"></blockquote id="quote"></font id="quote">

Thank you for the time and effort you invested in my problem. I had already found this article, and tried varying the sequence of the circuits; I think I will try this again. I'm trying to avoid digging up the system to increase the pipe size or add more circuits, though that's probably the surest solution. Your earlier response recommended using Superior Brand valves. I found their website and they advertise slow closing on their valves. Does your experience with them under high line pressure verify their claims? I'd be willing to try them if you know they work well. Thanks again.

Wednesday, August 8th 2007, 7:28am

by mrfixit

After reading this article again, I'm thinking that's where I got the above idea from. I guess this is how senility starts. =) The article has some interesting solutions. --
http://www.irrigationtutorials.com/waterhammer.htm

Tuesday, August 7th 2007, 10:35pm

by Wet_Boots

I don't think there's much effort in manufacturing valves to close slowly on high supply pressures. Easier to correctly design a system from the start. Reduce the flow on the hammering zones, and the hammer will also be reduced.

Tuesday, August 7th 2007, 5:40pm

by mrfixit

Let me throw out an idea. I've never tried this or heard of it. Let me know if where the idea goes wrong. I believe water hammer is caused by the amount of flow and speed of the water. What if I increased the pipe size before the manifold. For example, the manifold and main line leading to the manifold is 3/4 inch. What if I put a piece of 1" pipe in the mainline before the manifold. Let's say? 6 feet? Or even 1 1/4 inch. Would this slow the flow down enough to stop water hammer?

Tuesday, August 7th 2007, 2:43pm

by jmduke7

Can't remember the name of the valve (thinkin' it's a Watts Regulator Brand Valve) but it has a bypass that regulates the pressure that activates the diaphragm (Not a pressure regulating valve). In a since, it would reduce the pressure to a more manageable amount inside the valve to eliminate the water hammer (how fast and slow the diaphragm closes). I will have to dig around and find it again, and It may be too expensive of a cure.

Tuesday, August 7th 2007, 2:00pm

by mrfixit

Oh man water hammer. It's one of my worst nightmares. I've tried everything. But you did mention the only way I've ever been able to cure it. By installing slow closing valves. Since you have such a high water pressure and you're using anti-syphon valves, I recommend you go to an all brass valve. A brass anti-syphon valve body with Superior brand valve adapters. It's the 800 series. They close slow and can easily handle the pressure. It's an expensive fix and no guarantee it will completly cure the problem but no doubt it will help. I hope the other guys chime in with ideas. I'd like to hear them. Also I read a water hammer article recently. I'll see if I can find it and I'll post a link for you.

Tuesday, August 7th 2007, 1:42pm

by BobD

Water Hammer Problem

We bought a home with the sprinkler system installed by the previous owner. The local water pressure is 120 psi. One of the existing valves blew apart after 10 years of service. I replaced the old valves with RainBird 075-ASVF rated at 150psi. But several lines have a significant water hammer when the valves shut off. I tried using a pressure regulator to 80 psi, but then there is not enough pressure to feed the existing circuits. I removed the regulator and tried varying the sequence of the circuits with little improvement. Water hammer arrestors would have to be very large to handle this pressure. Are there any valves that can handle this pressure with a gradual close? Are there any other ways to reduce the water hammer without redoing the whole system [?]