Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.
Attention: The last reply to this post was 4276 days ago. The thread may already be out of date. Please consider creating a new thread.
The last 5 posts
2 Valves Open at Same Time
Turned on each valve manually & they are working independently. So the water lines are not crossed. It is the wiring causing the problem. But I can't see or find any place where the casing is torn or wires are touching in the area where I fixed the water leak. How do I trace the wiring? Start digging? My back hurts just thinking about it.
Or can I test with a multimeter? Of course the system is 20 years old, maybe some new wiring is in order.
You said you moved some wires around. Maybe the casing has come off the wiring and now two wires are touching when they're not supposed to.
Is there a master valve? Do the zone valves have flow controls?
My first step would be to confirm it's the wiring.
Find the valve for either zone. Turn the bleed screw or solenoid and turn it on manually.
Do both zones come on? If so they are cross linked in the piping.
If not you have to start tracing wires.
2 Valves Open at Same Time
I have 2 valves opening at the same time to 2 separate zones. My water presure is not strong enough for 2 zones. Just started doing this after I fixed a break in a water line. I did not do anything to the wiring except move it around while digging to fix the line. I disconnected the wire at the controller for valve 1 but they still both came on when I turn on valve 2. I reconnected valve 1 & disconnected valve 2 but still they both came on when I turn on valve 1.
It seems to be an electrical issue but I don't understand how the power is turned on from the controller to 2 valves at the same. Anyone got an idea how to troubleshoot this?