You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 7580 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 10 posts

Sunday, July 27th 2003, 11:30am

by Rays Sprinklers

Glad everything works!

Thanks
Ray
Rays Above and Beyond Automatic Lawn Sprinklers

Tuesday, July 15th 2003, 4:33pm

by tmostad

Mystery solved. I finally got a chance to disassemble the valve and there was a small rock on the ledge where the diaphram seals. It was just large enough to keep the valve open once it was opened by the solenoid but when I closed the downstream mechanical valve the flow was stopped and the diaphram would reseal. Any larger and the valve would never seal and any smaller it would have gone unnoticed. Obviously Rainbird gave me bad info because the valve works just fine now. Thanks again for the suggestions.


Saturday, July 12th 2003, 11:24am

by Rays Sprinklers

If none of that works, try installing check valves on those heads for that valve


Thanks
Ray
Rays Above and Beyond Automatic Lawn Sprinklers

Thursday, July 10th 2003, 11:24am

by drpete3

Another thought that I had was to use an antisiphon valve. I am not sur exactly how they work but I Know that rainbird makes one and I am using them. I am just not sure if they will relieve the neg pressure.

Thanks,

Pete

Thursday, July 10th 2003, 10:02am

by tmostad

Thanks for the responses.

The negative pressure is never relieved, i.e. the water in the line apparently keeps the valve open by suction which releases more water which keeps the valve open, etc. and the valve never closes (water continued to flow overnight after power was removed). I thought about putting a drain valve in-line right after the 100-DS but wasn't sure how the dynamic would work. I think the suction might pull it open and allow air into the line breaking the suction. I will try this if all else fails.

The valve is *far* above the highest sprinkler, about 60 feet.

I know the valve is fully closed, i.e. turn so it is not manually on. There is no leakage at the valve therefore I don't think the bleeder valve is open but will check. I have 15 other valves in the system and none exhibit this behavior but also none of them are in this uniques situation. I will diassemble the valve and clean it/check the diaphrams and screens.

The guy at Rainbird was emphatic that I had made a grave mistake and implied I should have hired a contractor to do the work and was really stupid for not having done so. It was really a quite amazing conversation.

Thanks again for the suggestions.




Thursday, July 10th 2003, 10:00am

by tmostad

Thanks for the responses.

The negative pressure is never relieved, i.e. the water in the line apparently keeps the valve open by suction which releases more water which keeps the valve open, etc. and the valve never closes (water continued to flow overnight after power was removed). I thought about putting a drain valve in-line right after the 100-DS but wasn't sure how the dynamic would work. I think the suction might pull it open and allow air into the line breaking the suction. I will try this if all else fails.

The valve is *far* above the highest sprinkler, about 60 feet.

I know the valve is fully closed, i.e. turn so it is not manually on. There is no leakage at the valve therefore I don't think the bleeder valve is open but will check. I have 15 other valves in the system and none exhibit this behavior but also none of them are in this uniques situation. I will diassemble the valve and clean it/check the diaphrams and screens.

The guy at Rainbird was emphatic that I had made a grave mistake and implied I should have hired a contractor to do the work and was really stupid for not having done so. It was really a quite amazing conversation.

Thanks again for the suggestions.




Tuesday, July 1st 2003, 12:30pm

by Rays Sprinklers

Sorry, it should say the negative pressure SHOULD NOT cause that

Thanks
Ray
Rays Above and Beyond Automatic Lawn Sprinklers

Tuesday, July 1st 2003, 12:28pm

by Rays Sprinklers

Hey,
I did some research with rainbird. Its funny because when i caleld as a contractor (im regestered with them) they gave me tons of advice, but then i caleld as a homeowner and didnt get as mch, i guess it depends on the person. First, is the valve 12" above the highest sprinkler heads?? is the manual bleeder closed all the way? is the soloniod closed all the way?? The negative pressure should cause that. OPen the valve clean it, make sure there are no tiny holes in the diaphram, and flush the lines. It may just be a bad valve. Assuming this isnt a 1 zone system, do the other valves to this??



Thanks
Ray
Rays Above and Beyond Automatic Lawn Sprinklers

Tuesday, July 1st 2003, 7:59am

by drpete3

How long does it take for the valve to close?(when is the negative pressure relieved?)
What if you were to put a harmony drain at the top of the hill with the drain up side down and above ground. My thought is that this might work like the little opening on the back of a five gallon gas can and relieve the neg pressure.


Monday, June 30th 2003, 1:12pm

by tmostad

Negative pressure prevents valve closure

I have a line with a long downhill run and a 100-DS valve at the top. When power is removed the valve doesn't close. I called the 1800RAINBIRD line and he confirmed my guess that negative pressure is preventing the line from closing. He offered no advice. Anyway, being an engineer, I could design a circuit with another valve that would open momentarily when power is removed to break the suction long enough to let the valve close but hoped there might be a ready made solution. I thought maybe it would be possible to increade the spring tension in the valve to help it close better. Please don't tell me I am an idiot for designing and installing my own system and making a simple mistake. The Rainbird hotline guy already did that.

PS - I am fully prepared to replace the valve with a different/better one if necessary.



Edited by - tmostad on Jun 30 2003 6:17:44 PM