You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 6823 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 7 posts

Friday, September 2nd 2005, 5:54pm

by Jazzer K

what you need to do is buy a voltage tester and turn on on zone and check your feed and the common and see if you have 24 volts. That should help if you have any thing less than 24 volts that will not open the valves. Check wiring.

Thursday, April 7th 2005, 9:16am

by nestors

replace timer with a hunter pro-c .

Monday, June 21st 2004, 11:52am

by alect

Checked with a voltmeter. Found that controller had power going in but no power coming out. Replaced it with a Rainbird controller (basic model). Thanks to all for your help.

Tuesday, June 15th 2004, 4:55pm

by radical

Volt meter is essential when trouble shooting an electric valve system. MRWETTECH gave you the correct process. Hopefully it's not a cut wire. If I were you, I would invest in a better timer if that's the problem ( and send the Orbit into orbit ). Rainbird, Toro or Hunter I would recommend (Not from Lowes or Home Depot!)

Saturday, June 5th 2004, 3:40pm

by alect

<blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by mrwettech</i>
<br />Always start at the controller and work your way out. Use one of those solenoids or a voltage meter and check the controller. Turn zone #1 on and test the wire terminals in the controller. One wire to the common the other to #1 terminal. It should activate the solenoid or read 24v on the voltage meter. If you are good there start working your way to your valves. Is there a rain sensor on your system? Has there been any new plantings or any sort of digging since the last time it ran? Start there and let us know what you find. This just part of the trouble shooting process. I hope this helps.
<hr height="1" noshade id="quote"></blockquote id="quote"></font id="quote">

looks like I will need to get a voltage meter - have changed solenoids so they're not the problem. It seems I have two options:- get a voltage meter and try figure out where problem is - if am lucky then controller and I just buy a replacement. If not and there is something wrong with the wiring, I will be forced to get new wireless (battery) controllers as I don't want to dig up.

Will report back.

Thanks.

Friday, June 4th 2004, 3:31pm

by mrwettech

Always start at the controller and work your way out. Use one of those solenoids or a voltage meter and check the controller. Turn zone #1 on and test the wire terminals in the controller. One wire to the common the other to #1 terminal. It should activate the solenoid or read 24v on the voltage meter. If you are good there start working your way to your valves. Is there a rain sensor on your system? Has there been any new plantings or any sort of digging since the last time it ran? Start there and let us know what you find. This just part of the trouble shooting process. I hope this helps.

Wednesday, June 2nd 2004, 8:05pm

by alect

Help with sprinkler

We bought a house with a 2 station system in the back. It has stopped working.

I have checked the controller (Orbit) and it seems to be working fine. But even when I set it to Manual, the sprinklers don't work.

If I turn the sprinklers on manually (at the valve)they work fine).

So I went and bought replacement solenoids. Installed them. But still no go.

My questions is: Does this sound like there is a problem with the underground wiring (in which case I can't be bothered digging it up). Or is there something else I should check? (easily)