You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 6590 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 5 posts

Tuesday, April 18th 2006, 4:17pm

by pilotjohn

Found the Problem. When I took a VOM to the 3 circuits it read all 0's. I traced the wired and put new grease wing nut fittings on them. These are the good expensive ones at about $1 each. I have surmised that the original installer did a terrible job of wire connection at the solonoid wires. He used cheap grease wire nuts. This solved the problem. I will now redo all the solenoid wires.
Thanks much for your advise.
John

Monday, April 17th 2006, 4:03pm

by pilotjohn

This is their third year of operation.
John

Monday, April 17th 2006, 4:02pm

by pilotjohn

Two are together in the same box, but one is in another box with one working and the other is not. No digging lately. Thanks

Monday, April 17th 2006, 2:47am

by SprinklerGuy

Could be many things....

Are the 3 valves together in the same area...and away from the 5 that work?
How old?
Any digging lately in the yard?


The valves operate using 24 volts of AC current...sent through wires from the controller to the valves....the current opens the solenoid (the thing w/ wires on the top of the valve)....once the solenoid pin pulls up into the coil itself....water comes off the top of the rubber diaphragm in the valve allowing it to open and water.

most common problems:

Wires cut to solenoids
Bad solenoids (especially the first couple years of Hunter solenoids)
Bad diaphragms


The fact that you can turn them on manually...sorta makes me think bad solenoid, but not necessarily...more info please.

One test for the solenoids involves an ohm meter...auto ranging is easiest...have one? If so, go to the timer...set the multimeter on ohms....put one probe on the common wire in the timer..one probe on the station wire(s) in question...it should read between about 25 and 45..anything lower or higher, could be troubles. If no reading at all..wires are cut.

Let us know

Saturday, April 15th 2006, 3:50pm

by pilotjohn

Sprinkler zones not coming on

I have 3 zones with Hunter SRV valves that will only come on when I turn the round knob to open. All other zones (5) work with the timer just fine. What could be wrong with 3 zones?
Thanks,
John