Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 6955 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 3 posts

Tuesday, April 12th 2005, 2:23pm

by RidgeRun05

You may have a short in your wiring. Like water miser said, you should be reading 24 VAC between the common and zone terminals. Have you done any digging or construction in your yard since you have been having this problem? If so, maybe a wire has been cut.

Monday, April 11th 2005, 5:09pm

by water miser

when that particular zone is calling to be on,you should read 24v +/- 10% between common and that zone terminal. remove that zone wire make that zone call if 24v is between that zone terminal and common,you know the controller is good.if your reading almost 0 volts with the zone calling you have no potential difference meaning you're reading the same leg with your meter.it's like putting your meter across a live fuse to read volts you'll read 0.disconnect valve solinoid and controller ohm out wires if there's continuity it's a bad wire.i would suggest to call a pro.i try not to make a habit of giving step by step instructions because us contractors have to eat too.

Sunday, April 10th 2005, 3:47pm

by Philip Ronney

Valve not responding to electronic signal

I have an older model Rain Dial we installed in 1992. One of the valves simply won't work and I'm stumped. I took a meter reading of the two wires going to the actuator and it measures between 12 and 13 volts with the actuator turned off. It measures almost zero with the actuator on. That seems correct to me. I put on a new valve with a new actuator and it still doesn't work. All the other 11 valves in the system work just fine. What am I missing?