You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 5102 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 5 posts

Friday, April 30th 2010, 11:48am

by ablkop

Thanks all for your advice and information.

Thursday, April 29th 2010, 9:20am

by HooKooDooKu

If you are having issues with water pressure and you're trying to minimize pressure loss, you would want to compare pressure loss charts for different sizes to see which has the least pressure loss for your designed flow rate. Counter to what you might think, there are times where you will get less pressure loss at a given flow rate in a back flow preventer that is SMALLER that one that is bigger, especially if you are looking at RPZ devices.

If marginal water pressure isn't an issue for you, then you fall back on Wet_Boots advice and use the size that is most conveniant.

BTW, the same advice applies to sizing valves.

Wednesday, April 28th 2010, 8:59pm

by Wet_Boots

Backflow preventers are flow-rated the same as water meters are, which means they can pass much more flow than you would normally have in a pipe of the same size. For a PVB, you can match the supply size of the pipe coming into the water meter, and not be killing system performance. The reason you see a lot of one-inch PVBs on systems fed from 3/4-inch plumbing, is that the zone valves will be one inch, and the plumbing is simplified by using all one-inch.

Wednesday, April 28th 2010, 6:37pm

by pass1

Size selection is based on your allowable pressure loss through the device as well as the velocity,usually around 7-8 ft./sec. Both inlet and outlet are the same size.

Wednesday, April 28th 2010, 3:10pm

by ablkop

PVB sizes

When seaching for PVB devices, what determines that size? The opening for the incoming H2O or the opening for outgoing H20 or are they the same for both?



Thanks :thumbup: