You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 4680 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 6 posts

Monday, July 11th 2011, 12:16am

by Mitchgo

It's possible the intake has a small leak and sucking in air, preventing your pump being fully primed.

Saturday, July 9th 2011, 2:57pm

by Wet_Boots

If you want to get technical, you get a vacuum gauge and see how it reads when you connect it to the suction side. I had a clogging problem on a well point, and doing the backwash process got my as-new performance back. I had to repeat it every other year.

As for pumps, Home Depot and Lowes are not on my radar, so I don't even remotely care about anything they sell. I install cast-iron jet pumps made by Goulds.

Saturday, July 9th 2011, 2:38pm

by jskjolda

Still Not Working

I have back washed the point 5 times, reprimed and still not much luck. I wonder if it could be the "new" pump? How do I tell it's working correctly? I am now also thinking about driving a new well. If I go with 1 1/2 inch point what size pump should I be using? If I go with a 2" point?

Any suggestion on brand of water pump?

Thanks

Friday, July 8th 2011, 3:34pm

by jskjolda

Thanks!

I am trying that now. I am back washing under pressure. Turning hose on/off. Initially I felt resistance when the water got to top of pipe. Now I have a gentle flow into the well. I will see what happens..

Friday, July 8th 2011, 3:24pm

by Wet_Boots

Well points can get clogged up, and you have to try to flush them clean by forcing water into them, to blow clogging particles away from the screen.

It's a repetitive process. You backflush. You let the pump draw water. You back flush. You pump. So on and so on.

What you are trying to achieve is to get as many small particles as possible into the well point and through the pump.

If you have a clear-body strainer on the pump outlet, like a Vu-Flow, you can tell when you are no longer bringing up extra particles through the pump.

Friday, July 8th 2011, 10:06am

by jskjolda (Guest)

New Well Pump Help

I live on Long Island NY. I am in a sandy/clay soil area. About 10 years ago I hand installed a 2" well point down to about 25 feet with galvanized pipe. Water table is abut 13 feet so I have plenty of water in the pipe. I was using a 1.5 HP centrifugual pump to provide water to my irrigation system. I noticed a drop in pressure this season. I had a new 1.5 HP WaterAce pump in the basement so I installed it. After I did, I wasn't gettin any water after multiple priming attempts.
I then replaced the check valve, opened the well pipe and tried to flush with a hose doen the pipe. I did get some sediment out. I reinstalled everything and reprimed. I am flowing water but no where near what I was with the old pump and what my needs are. I have looked for air leaks in the above ground piping and have not spotted any.
The well was outside my house when I drove it. It is now under a crawl space so my work space and options are limited. Short of driving a new well outside the house again is there anything I can do?
I am at wits end with this. It's 90 degrees and sunny .. and my grass is turning. What can I try?
Thanks ... John