a 1HP submersible drawing at 180 feet isn't going to match what can be drawn from well points with the water only ten feet down
In any event, it isn't likely that the existing system is piped to make efficient use of greater flows.
You could make use of as many as three pressure gauges -
one with a "pitot adapter" for field measurements, and two for the booster pump, located on the inlet and the outlet. By logging pressure readings for each of the zones, you can get an idea of what losses are occurring in the field plumbing, and what the original well system is doing, before the booster.
In general, you are probably going to look to reduce zone flows, with the result of raising supply pressures. The reason for this, is that you haven't mentioned that you have any sort of backflow prevention assembly on the system, and correcting that deficiency will cost you some water pressure.