Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

segask

Active Member

Posts: 9

Location: USA

1

Tuesday, October 28th 2003, 7:21pm

master valve and backflow preventer

I'd like to have a master valve on my system. My backflow device would be a PVB. Is it alright for the master valve to be in front of the PVB? Or does the PVB need to be under constant pressure in front of the master valve? I was wondering because the online installation guides at Watts Regulator website says that to properly place a PVB into service you first open inlet valve to pressurize the PVB and then open the outlet valve. If I had master valve opening and closing all the time in front of the PVB, then I guess the PVB would spit out a bit of water every time right? But would it prevent the PVB from properly protecting against backflow?

RVLI

Supreme Member

Posts: 462

Location: USA

2

Wednesday, October 29th 2003, 12:45pm

Here is what I do:

Install the PVB, then take the pipe down into the ground and elbow it. Add a foot or so of pipe to that elbow then thread/glue on the master valve. It's better off to just install it after the PVB and put it in a 6" valve box.

Rays Sprinklers

Supreme Member

Posts: 493

Location: USA

3

Friday, October 31st 2003, 12:14pm

Definatly after the PVB. Not only does the PVB need to be before everything, but you are right that when the valve opens and closes there is a chance the PVB will start gishing water. It has to be under constant pressure