Let me start by saying that I did read through most of the threads but still my questions is not quite answer yet.
Here we go.
I have 11 zones and they're typical 4-5 heads each. Last two years I watch the lawn companies guys come in with huge air compressor and blowout my lines, zone by zone. I figure I could save some money and also have an air compressor for use on the side as well.
30 gallon 7.7cfm @ 40psi.
When I ran zone 1 about 3 times, it watered up and then turn fine mist and then no mist. Great, same for 2 and 3 and so on, but some zones no water comes out, but the head pop up blowing air, I can see the head pop up even though there's nothing coming out. It's zone 10 that scares me, it doesn't pop up at all and no mist, no water, but I can hear the air at each head.
Does the zones drain the water into other zones once the other zones are empty? and/or does the higher(elevation) zones sink/flow(gravity) down into the lower zones because theres little or no water in those zones? When the commercial guys do it, I see water from every zone come out and they do it in the same order that I do. My gut says zone 10 should/might still have water, but I can't confirm and also, my zone 1 blew out a lot of water compare to the rest as well?
Obviously i have to let the compressor recharge to full tank between blowouts, but I keep the pressure at 70 and as soon as i plug in the air, it quickly drops down to 40 and I increase the pressure back to around 60. Pretty sure I didn't blow any up with higher than 60-65 psi.
What are you guys experience?