Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

11

Friday, April 28th 2006, 5:42am

What you were looking at, so far as Hunter PGPs go, I don't know. Obviously something less than a complete picture, since the larger nozzles on a PGP will make it use over 14 gpm. The various PGP nozzles allow you a good deal of wiggle room. By the way, you don't have an absolute need for head-to-head spacing, except in cases where the sprinklers have to be set a ways from a border, like with a belgian block curb. The design you have could still work, even with less than 30 feet radius from the PGP's

Even with a 3/4 meter, you can probably use less zones that the design shows. Make the connection anyway, and take measurements. The maximum rated flow of a genuine 3/4 water meter is 30 gpm, (a 5/8 meter's is 20 gpm) so you still have a good chance at more water than the design allowed for. If your supply line size is one inch, you might look to get a one inch meter installed. Sometimes, you can even get the water company to make a new tap on the water main, and bring in the one inch connection. (Prices for this can vary, obviously)


jlease

Senior Member

12

Wednesday, May 17th 2006, 11:53am

DOORZ, have you finished your design and done the install yet?