Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

New2thePark

Active Member

Posts: 7

Location: USA

1

Tuesday, May 24th 2005, 12:57pm

Sprinkler Layout

Greetings!

My name is Ryan and I am a licensed plumber by trade and hope some of you pros might be kind enough to help another pro out. My mother, now 78 years old, can no longer take care of her yard, which is where she likes to spend her time. While I've been more than happy to mow and groom, I just can't make it over enough to keep it properly watered and last year it looked terrible and she was heart broken. I wanted to have a sprinkler system installed for her, but after getting 4 quotes from $3600 to $4100 I just can't afford to with my business, a beautiful wife, 4 wonderful kids, and a fat mortgage. Mom's retirement can't fund a creature comfort like that either. So, I'd like to tackle the installation myself since I can pick up the components at cost. After doing much research on the internet and asking the pros I install taps, backflows, and boosters for, I think I'll stay with RainBird and Hunter equipment. I'd also use poly pipe and already own two Ditch Witch trenchers for the business so that's not an issue. I've studied the Hunter design guide as well as www.irrigationtutorials.com, but am having trouble coming up with a sprinkler layout that covers this divided and skewed property:



Also, I'm certain there will be need for multiple zones with the house on city water with static pressure of 50psi and flow at 8 GPM (new 1" polyethlene from the street main to 3/4" copper in the basement just before the 5/8" meter). I'd appreciate any suggestions. I've also sent the plan off to RainBird for a layout, but won't see that back for a while, but I learned today that due to construction delays I have this upcoming weekend completely open to work on it.

RidgeRun05

Supreme Member

Posts: 314

Location: USA

2

Tuesday, May 24th 2005, 4:18pm

Ryan-
Looks like you've got a pretty decent start to your irrigation system. Good drawing, and you've done your homework as far as measuring water pressure and flow rate. (Which I would expect from a plumber!) I would suggest the Hunter products, but both Hunter and Rain Bird make a decent product.

For your front lawn area on both sides of the driveway I would suggest using rotor type sprinkler heads. Either the Hunter PGP or I-20, or the Rain Bird 5000 series, both of these sprinklers work well with the water pressure and flow rate provided. Same goes for the backyard, I would use a large turf rotor such as those listed above.

For your three strips of lawn on the outside of the sidewalks, I would use a spray type sprinkler head. The Rain Bird 1800 series is a good choice, but Hunter has recently come back with the Pro Series spray heads. They have a much better wiper seal and a much better spring in them, which in turn leads to better retraction of the sprinkler head after the zone turns off. (The 1800 series often has a problem of sticking up after the water is off).

For your controller I would suggest the Hunter Pro-C, it by far has the most amount of options and is very easy to use and program.

You are correct in the fact that you will need multiple zones, without proper dimensions, I couldn't tell you exactly how many, but you will need multiple zones. Also, because of the different precip. rates, you will want to seperate your rotor sprinkler heads from your spray type sprinkler heads. Any other questions, let us know.
Tony Posey
Ridge Run Landscapes

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

3

Tuesday, May 24th 2005, 4:32pm

A static pressure of 50 psi makes it important to take steps to conserve pressure. Is the poly main IPS or CTS? (poly mains? where is this?) Can the 5/8 meter be swapped for a 3/4? (or one of those 3/4 meters in a 5/8 size) - Hopefully the property is flat, so a Pressure Vacuum Breaker will suffice for backflow prevention.

Design begins with locating heads at the corners and filling in the gaps. Heads will not have much pressure, so don't skimp on the spacing.


New2thePark

Active Member

Posts: 7

Location: USA

4

Tuesday, May 24th 2005, 5:39pm

Wet Boots,

This is in southern New Jersey - flat is all we have! PVBs are standard in this area for sprinkler systems. As for the supply, recently (year and a half or so ago) the mains were replaced in my mom's neighborhood and all service connections went to polyethylene in accordance with ANSI/AWWA C901 so IPS. Actually, pretty common here now.

The problem with a meter swap also means a higher service/usage cost.

RidgeRun05,

To give you a perspective, the driveway is 20 feet wide and 35 feet long from the house to the road (i.e., including curbcut). Any tips/suggestions how to place/aim Hunter rotors in the front lawn to the left of the driveway (from perspective of facing the front of the house) so as to not drown mom's porch? If I place them in all the corners it looks like the specified radii for the rotors will cast onto the porch to go head-to-head. Could I triangulate that area with one in each of the front corners set to cast in a partial arc short of the porch then use a 3/4-circle rotor at the corner of the planter and then just pick up the little piece in the left adjacent to the fence corner with sprays since that's probably the best way to cover that side of the house behind the fence? Piecing the resources together, it would seem to me that the corner rotors could use a No. 4 nozzle on a PGP and the 3/4-circle a No. 8 and this could be one zone. Am I in the ballpark or back to the studies?

Thanks!

RidgeRun05

Supreme Member

Posts: 314

Location: USA

5

Tuesday, May 24th 2005, 8:37pm

Ryan, Is this what you had in mind?
Tony Posey
Ridge Run Landscapes

New2thePark

Active Member

Posts: 7

Location: USA

6

Wednesday, May 25th 2005, 3:44am

Yes. Would that be reasonable to cover the primary area? I was then thinking a spray at the outside fence corner connected to a zone of muliple sprays to water the strip between the fence and the house/deck on that side.

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

7

Wednesday, May 25th 2005, 6:54am

Uhh, problem. You may not be able to confine the spray from a Hunter PGP-#8 to less than a 20 foot radius.

Your situation is a little different than what a contractor with a pipe puller might be looking at. The amount of trenching you'll do won't directly relate to the number of heads. So skimping on the number of heads you use is a pointless economy.

You have 50 psi static pressure. Through the sprinkler plumbing to the heads, you will lose 10 psi. (pipe, PVB, electric zone valve) - So, at the most, the sprinkler heads are looking at 40 psi. And you haven't even turned the water on yet.

This is why I asked about the supply line and the meter. You can get 15 gallons per minute through that line with no problem (and a pressure loss of about 3 psi) Now we get to the water meter itself. AWWA standards for a 5/8" water meter at 15 gpm is 8.3 psi. For a 3/4" meter, it's 3.6 psi

So switching to a 3/4 inch meter buys you as much as five psi extra, making it worth the money (your consumption will cost you a lot more than the base meter charge anyway) From my observations, you don't get nailed until you move up to a one inch meter. (everyone's mileage will vary) By the way, you want to check and see if you face a sewerage surcharge based on your water meter reading. If so, you get a secondary water meter, feeding only the sprinkler system.

For flat properties, it is also possible to ditch the PVB and electric zone valves, for the individual electric anti-syphon valves. The change gains you a few psi (less than five) and costs you no extra. Antisyphon valves are ASSE approved, so they will comply with the National Standard Plumbing Code. The industry standard antisyphon valve is the Irritrol 2713APR (they make a jar-top 2713DPR, but insist on the APR model) - Rainbird also makes antisyphon valves. Antisyphon valve use is not all that common, nationwide. They're common in California, and no one there minds the look of a row of above-ground valves. In some other areas, the sight of any above ground plumbing runs into customer resistance.

Being in southern New Jersey, it is likely you have sandy soil. Hunter heads do not love sandy soil. (few sprinkler heads do)

Given all the conditions, this is a job done best by using mist heads. They'll perform at pressures the rotor heads do poorly at. They will water at a rate compatible with thirsty sandy soils. They will fit oddball spaces like the strips between the sidewalks and the street. Also, mist heads can be fitted with variable-arc nozzles, for those not-square corners. For decades, the Rainbird 1800 popup mist heads have been the best you could get, because of their patented popup seal. If that patent has run out, then the other guys may catch up. (it may be that Hunter's imitation of the 1800 is successfully making an end run around Rainbird's patents) With today's longer grass lengths, use the 1804 head. I've used the 1800 is all sorts of soil conditions, and their pop-down capability is why the other guys chose to imitate Rainbird's head.

It will be more time and trouble to install an all-mist-head system, but not much more money, with you doing the work. The results will be worth it.

New2thePark

Active Member

Posts: 7

Location: USA

8

Wednesday, May 25th 2005, 7:46am

Wet Boots,

First, thanks for this help! I'm sitting here in my shop with lunch thinking about this some more... You mention going to an all-spray set-up, which is actually something I had originally considered, but the pro installers I chatted up said they wouldn't do it that way. Well, that's no technical answer, but those guys do it every day. For me, I don't care about the labor for mom. I just want a system that will function as intended and keep the green! I'll trench a mile if need be. [8D]

I know, very low pressure. Mom's usage actually wouldn't offset the upsized meter in her Boro, and to add a second means a second service connection, corp stop, etc., but more importantly a street-opening permit and all the ancilliaries to restore the paving = $$$ even if I do all the work. Is it really fruitless to try to design with the supply as-is? I can't believe so seeing as how I tap and install PVBs on the very same configuration at least twice a week in the Spring growing season - 1" (various materials) from the street to 3/4" copper and a 5/8" meter is considered the residential standard around here... If I must, 3/4" meter would be the lesser evil, but will just about double the water bill. I know, I know, trade-offs. I suppose I could have the engineer who calculates my piping for me look at it...

As for the anti-siphons, no can do. The local code modifications do not accept their use. In fact, for existing system with them, they have to be changed out or the system abandoned when the property changes hands or a CO will not be issued.

Jersey soils are sandy indeed, but the topsoil that was imported when Dad built the home is a good loam. Everyone I talked too suggested I'd be A OK with everything Hunter except go with Rain Bird 1800-series sprayers without debate. Seems to be consistent with everything I've found on the internet too.

Now an installation question. I will be using poly pipe. Are the piercing saddle-type fittings the way to go? Also, I'm a fan of minimizing joints so was thinking not to use funny pipe and just use cut-to-fit nipples. Should I incorporate automatic drains? I intend to blow out the system for winterization as I have a large mobile compressor I use to pressure check piping.

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

9

Wednesday, May 25th 2005, 9:27am

Pros wouldn't do an all-mist-head system because of the additional labor involved with the extra heads. (and zones, pipe, and valves) The price becomes uncompetitive.

As for water meters and anti-syphon valves, this is a case of local practices. In fact, the code I cited specifically allows for localities to set tougher standards. And since atmospheric vacuum breakers have been so misused in the past (and today, too) the local dislike of them, and the antisyphon valves, is understandable. (but their use is still in compliance with the requirements of the various regional codes - they ought to, being that they work on the same gravity basis that PVB's do) The secondary water meter is worth running down, however, until you have something definitive in writing, from the appropriate town official. (if no official policy exists - this might be an opportunity to start one) Obviously, all town water usage must be metered, but the significant sewerage charges that are keyed to meter readings have made the separate sprinkler meter (from the existing supply line) more commonplace. Towns don't lose out, because they get enough money from the secondary meter installation to cover their costs, and they sell more water, and also avoid motivating a homeowner toward looking at well water. A few towns I know of handled the sewerage-charge complaints in a simple fashion, by using a wintertime quarterly meter reading to calculate the entire year's sewerage. Just a heads-up to make sure you aren't assuming it can't be done. It is money. If you're stuck with the 5/8 in the supply, you just have to get by with less water, and more sprinkler zones. With richer loam soils, you don't need as heavy a soaking as pure sand wants.

Your best possible work with poly pipe will be with clamped insert fittings (and not the ones that a Home Depot sells) - use funny pipe, brand name funny pipe elbows (Rainbird, Toro), and marlex elbows at each head. Skip the drain valves, and if you use a large compressor for winterizing, regulate the pressure to 50 - 60 psi.


New2thePark

Active Member

Posts: 7

Location: USA

10

Monday, June 6th 2005, 11:43am

Well, it's DONE! At least the install... My engineer sat down with me and we hammered out a plan that seems to have fit the bill perfectly. About 2000' of poly pipe and a bunch of prefab swings joints. Ended up with 11 zones using 21 rotors and 34 sprays considering the water availability. Coverage seems to be very good on a zone-by-zone basis. Now I just need to get the programming right, but the Pro-C is pretty easy to operate.