Backflow preventer

I have a Febco vaccuum pressure breaker. When I try to run water through it always leaks out of the top. Is this because I don't have it level? It's not that far off. I have checked the parts inside and everything seems to be OK.

RVLI

Supreme Member

Posts: 462

Location: USA

2

Monday, May 13th 2002, 3:44am

<BLOCKQUOTE id=quote><font size=1 face="Verdana, Arial, Helvetica" id=quote>quote:<hr height=1 noshade id=quote>
I have a Febco vaccuum pressure breaker. When I try to run water through it always leaks out of the top. Is this because I don't have it level? It's not that far off. I have checked the parts inside and everything seems to be OK.
<hr height=1 noshade id=quote></BLOCKQUOTE id=quote></font id=quote><font face="Verdana, Arial, Helvetica" size=2 id=quote>
What's your pressure? If it's high do you have a Pressure Reducing PVB? If not you may need a new bonnet and or poppet set.


SprinklerGuy

Supreme Member

3

Tuesday, May 14th 2002, 3:24am

Is it gushing out of the top? Is it weeping out of the top? is it a new breaker? Was it currently winter there? Was it winterized? Is there a zone on when you try to turn on the breaker? Are you turning it on all the way, or cracking the valve partway? More info please?