Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

GMillas

Starting Member

Posts: 1

Location: USA

1

Monday, July 25th 2005, 12:43pm

Febco 825Y the problem?

I have high water pressure (120PSI) and I keep hearing what sounds
like a pressure relief valve blowing off momentarilly. Could the 825 be responsible for this? It is rated for 140 PSI could it need a rebuild? Has anyone experienced this before. It just did it again even with the sprinkler on?

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Monday, July 25th 2005, 1:36pm

The type of backflow preventer you have will do that at high pressure, which is why they are installed outdoors. It is not a malfunction. You can see the discharge after each zone valve shuts off.