Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

osha

New Member

1

Friday, August 16th 2002, 10:37am

Imperial 12 Station starts over

I recently bought a house with a very old Imperial Valet 11 station controller. Recently, after completing a cylce, the whole thing starts over again! Any ideas on why this is happening and how to prevent it?


nestors

Advanced Member

Posts: 110

Location: USA

2

Sunday, August 18th 2002, 9:43am

The clock just needs to be replaced ,even if you can repair it ,it will cost more than a New One . Nestor's... VPN1@attbi.com

vincent nestor
Vincent Nestor
Nestor's Sprinklers & Lighting
Alpharetta,Ga.30022



vpn1@bellsouth.net

www.NestorsLandScape.com
www.GeorgiaLighting.net

osha

New Member

3

Sunday, August 25th 2002, 11:18am

Actually, it didn't need a new clock. The problem was that I had the cycle running for under an hour and so the cycle began again. I extended the cycle to over an hour and no problems since. Seems like you should be able to run a cycle that lasts less than an hour, though.


Rays Sprinklers

Supreme Member

Posts: 493

Location: USA

4

Wednesday, July 30th 2003, 1:25pm

Yes Definatly anywhere from a minute on....i would replace with a Pro-C if you have a 12 station system!

Thanks
Ray
Rays Above and Beyond Automatic Lawn Sprinklers
Thanks
Ray
Rays Above and Beyond Automatic Lawn Sprinklers