Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

1

Sunday, March 30th 2008, 11:41am

Water Hammer Concern

I am about ready to start on my installation of a new system and am concerned about the potential of water hammer. I have for the most part over engineered the system to avoid > 5ft/sec velocities but there are a couple of areas that may exceed it. My water meter is only a 3/4 inch meter, but I tapped into it with 1" Sch 80 which continues thru the backflow preventer and then I move to 1 1/4" Sch 40 all the way to the valves. After the valves, except the master control valve I have 1" CL200. So the only areas of concern would be the section from the meter up to the backflow preventer. My static pressure is 70psi and the max flow is going to be 12gpm.

My main question is whether the velocity issue is only at the point of the valve closing or anywhere along the supply pipe. So does a valve closing quickly fed by an adequate size pipe create water hammer because the velocity farther upstream is > 5ft/sec.

Second question is whether or not hammer arresters are ever recommended or considered useful.

Thank you for any information you can provide me.

hi.todd

Supreme Member

Posts: 417

Location: Houston, Texas

2

Sunday, March 30th 2008, 6:50pm

I am not sure if I can answer all of your questions, but I will give some friendly advice that works down in Houston. Generally we run schedule 40 from the meter to the back flow device, and from the back flow device out we use class 200. Sometimes, we run schedule 40 all the way to the last valve (depending on the City Requirement), and then use Class 200. I have never run an entire mainline or from the meter to the Backflow in schedule 80. Schedule 40 is a little cumbersome to cut and work with, but Schedule 80 is going to be even harder to cut with in that application. Maybe I just need to get tougher. I don't know how long your pipe run is going to be, but if your only running close to 12 gallons per minute you may want to stick with 1". Usually, People start the pipe big at the water source to the back flow device, and then if you want to step down you can. You may want to keep the entire mainline 1" or 1.25", But if your mainline is 1" to the Backflow to go back up in size to 1.25" doesn't make a lot of sense. I know that you said your are over designing the system, but you can do a quality install with 1" and Below at a flow rate of 12 Gallons Per Minute. Your Distances and flow rate are key to friction loss. Known is the flow rate 12 Gallons Per Minute and that is good. Distance ?
This suggestion will save you a lot of Money in Material Schedule 80 is very expensive in the quantity that you will need. The time savings that you will enjoy in not working with schedule 80 will be pretty big.

Most Water Hammer that I have seen comes from homeowner Connecting in to the house water for the system at the house and not at the water meter. If you tie in at the meter or within a foot or two of the meter you should be in good shape.

I hope these ideas were Helpful :thumbsup:

Dan Todd
:thumbup: :thumbsup:

HooKooDooKu

Supreme Member

3

Monday, March 31st 2008, 8:34am

RE: Water Hammer Concern


...My main question is whether the velocity issue is only at the point of the valve closing or anywhere along the supply pipe...



...Second question is whether or not hammer arresters are ever recommended or considered useful...

#1. It doesn't matter where along the supply pipe you are exceeding "speed limits", it can cause a problem.

Water hammer is basically caused by water with excessive kinetic energy. Basically, when water is flowing, it has a certain amount of kinetic energy. When a valve suddenly closes, that water almost instantly quits moving. That kinetic energy has to go somewhere. One of the ways this energy is dissipated is by creating a pressure spike in the water pipes (hence the reason you want to use PVC rated for 200+psi even though your water pressure is 75psi). Kinetic energy doubles as water volume doubles. But kinetic energy quadruples when water speed doubles. So the real issue of violating the 5ft/sec "speed limit" is that water moving at over 5ft/sec has a LOT of kinetic energy in it.

When a valve suddenly closes, all the water behind that valve essentially crashes all at once because water is a virtually incompressible fluid. It's like a stack of workout weights dropped on the floor. It doesn't mater if you have a 10 pound weight on top of a 100 pound weight or a 100 pound weight on top of a 10 pound weight. Either way, you will have 110 pounds crashing on the floor at once.

Now water hammer has a lot of factors that go into it. So just because you have a section of pipe violating the 5ft/sec doesn't mean you are going to have water hammer. The valves you use will play more into it than the pipe. You can even get water hammer if all the water stays under the 5ft/sec speed limit. The reason is because the speed at which the valve closes has a huge impact on water hammer. Basically, a valve does not close instantaneously. During the time the valve is closing, it's like putting the breaks on the water and slowing it down. The "crash" doesn't happen until the point at which the valve completely closes. So if the valve closes slowly, it's like putting the breaks on a car travelling at a brick wall at 100mph. If the brakes are applied over a long enough time, the car might only be travelling about 5mph when it hits the brick wall. But if the valve closes quickly, it's like not putting on the brakes until you are 20 feet from the wall. Yea, you'll have enough time to slow down by maybe 10mph, but that means you'll hit the wall as 90mph. OK, I'm starting to ramble a bit on the subject, so at this point I'll refer you to www.irrigationtutorials.com. The author has a whole section where he attempts to describe the causes of water hammer. The only thing I have to add is that if you would have used 1-1/4" Sch 80 rather than 1" Sch 80, you'd be way below that 5ft/sec "speed limit". But if for sure you will NOT exceed 12gpm, the charts indicate the water will only be moving at about 5.35ft/sec. Not a gross violation of the speed limit, so you MIGHT be ok.

#2 As for an arrestor, that same web author pretty much claims that they never work. As I see it, those arrestors are like placing a spring on the front of that car heading towards the brick wall. If the car is hitting the brick wall at 10mph, adding that spring might help. But with irrigation situations, you're usually dealing with such large volumes of water, when water hammer occurs, it's usually because the car is hitting the wall at over 50mph. At that speed, a spring on the front of the car isn't going to make any significant different.

4

Monday, March 31st 2008, 12:17pm

Responses

Thank you for your responses. Unfortunately I could only access a portion of the line before the backflow preventer due to it going under concrete, but I did try to limit the amount of line at >5ft/sec just by common sense. I think I read in one of the irrigation tutorials that only a small length of restricted pipe is probably OK. I will be using Hunter HPV valves which claim to close slowly, I guess we will see. Thanks again.

HooKooDooKu

Supreme Member

5

Monday, March 31st 2008, 1:33pm

RE: Responses

...I could only access a portion of the line before the backflow preventer due to it going under concrete...
Could you just run a new line under the concreate? If we're only talking about a sidewalk, that should be easy. If we're talking a driveway, well that's more work, but depending upon your soil conditions, do-able. (I'll admit it took three days of work, but I was able to get a 1" pipe 18" under an 11' wide driveway with just a 20' piece of cheap rebar, 12' of black pipe, a few black-pipe fittings, and a 2# sledge hammer.)
...I think I read in one of the irrigation tutorials that only a small length of restricted pipe is probably OK...


The idea there is that you basically limit the volume of water running at the hyper-velocity. For fun, I ran the numbers to compare a fixed gpm running through 1" Sch80 pipe vs. 1-1/2" Sch80 pipe. The result is that the water running through the 1" pipe will have 2.5 times as much energy as the same length of 1-1/2" pipe.

...Hunter HPV valves which claim to close slowly...

Yea, they 'claim'. I have no experience with these valves, but I find the following two quotes from hunter's own marketing material interesting found at http://www.hunterindustries.com/Resources/PDFs/Product_Guides/Domestic/LIT224w.PDF

"while also slowing the closing speed to reduce the possibility of water hammer"

"thus eliminating possible water hammer"

So basicaly they first say "might help" and then later "will eliminate". Sounds like marketing double-speak to me.

This post has been edited 1 times, last edit by "HooKooDooKu" (Mar 31st 2008, 1:49pm)