Wire selection

You have various wire available by conductor. I intend to have 5 valves in one location. Am I to assume that I should be looking for wire w/ 6 conductors (w/ one neutral) or is this the total number of single wires in the jacket which would only support 3 valves?


RVLI

Supreme Member

Posts: 462

Location: USA

2

Monday, April 28th 2003, 3:57pm

How many total zones do you have? If you have 5 total zones, then you need a 6 conductor wire so you can use one for the common wire.


drpete3

Supreme Member

Posts: 376

Location: USA

3

Thursday, May 1st 2003, 8:17am

You need a 6 conductor wire. The one neutral wire is connected to every valve.

Thanks,

Pete

RVLI

Supreme Member

Posts: 462

Location: USA

4

Thursday, May 1st 2003, 2:58pm

They have wire all the way up to 13 strand. Also, if you want to expand in the future I would get larger wire now that way you don't have to replace it in the future.


Rays Sprinklers

Supreme Member

Posts: 493

Location: USA

5

Sunday, May 25th 2003, 5:13pm

i use thirteen strand wire, wether its 1 zine or 12. Basically thats not necessary but i only stock one roll, this is good for future add ons