Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

everett29

Starting Member

1

Friday, March 15th 2019, 11:19am

valve not working

I have 6 zones all are working except five I get an err code on the timer. If I turn the valve to on it works but will not work with timer

mrfixit

Moderator

Posts: 2,424

Location: USA

2

Friday, March 15th 2019, 10:25pm

Sounds like the solenoid's bad on the number 5 zone. Or the wires are crossed somehow.
Since you're turning on the valve manually, you know which valve 5 is. Try disconnecting one of the wires from the solenoid at the valve. Now go run it from the timer. Still get the err? No err = change the solenoid. Err = short, most likely bare wires touching. Look for bare wires while you're at the valves.