water spitting out from all 4 test cocks when installing Febco 860-100
I just installed my 1" RP, here is the layout: [font='"']I have a 3/4" copper inlet coming from the street to outside the house. I have a 3/4" 90 deg elbow which points up, a 1.5" nipple, changed the size to 1", a Wilkins 600 pressure regulator, filter, elbow, Febco 860-100 RP, PGV-101JT-MM Hunter Master valve, 90 deg elbow pointing down, 12" long nipple, 90 degree elbow which then gets changed to 1.5" pipe (which I don't have hooked up yet.
[/font] In testing the Febco, once I turn the water on from the source (master valve is closed) it starts shooting out water from all 4 of the test cocks. If I turn the master valve on manually, they stop spitting out water, but once I turn the master valve off the test costs spit out water again. I noticed that there are ball valves under the test cocks, I adjusted the center valve to stop the spitting, so am I suppose to adjust all of the valves to stop the water shooting out or is there something missing that I am suppose to do? I adjusted zones 3&4 to off, so none of the test cocks spit any water any more. Does it matter if the pressure regulator is mounted in front of the RP?
This post has been edited 1 times, last edit by "garyb" (Jun 1st 2009, 11:27am)
Under normal operation, test cocks should be closed. While I'm not familier with the febco model you reference (I'm just a DIYer who had easier access to Watts components), the test cocks I've seen are openned and closed with a screw driver. To close them, the screw driver slot should be perpendicular to the orientation of the test cock.
This just happened to me too. Water was shooting out of one of the test cocks, thanks for your post, HooKooDooKu. I I thought my double check valve was faulty. I didn't notice the little screw on front was facing the wrong way.