Zone running on its own

One of my zones just started magically running by itself and won't shut off. The electric is shut off to the system. I tried swapping out the solenoid on the R204 valve with no effect. Any suggestions? Am I looking at replacing the valve?

Thanks, Plymouth Jack

worachj

Advanced Member

Posts: 63

Location: Eagan, Mn

2

Monday, June 8th 2009, 9:33am


Most likely debris in the valve, try cleaning the diaphragm and flush out the valve.

Try this link for toubleshooting valve problems.
http://216.213.143.2/ProAuthor/ManProc.cfm?&sk=5A44C2F9%2D53AE%2D11DE%2D9261%2D00D0B789305D&&&ProcID=10691&ManualID=325&openMenu=10691