Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

trapkoch

Starting Member

1

Sunday, July 5th 2009, 10:20am

HR 6100 - both A & C stations running simultaneously

I'm using a Hardie HR 6100, with three stations on A and one station (drips) on C. When the C program is activated, however, the first station that is assigned to A also comes on. The programming seems correct (stations 1, 2, and 3 are only scheduled on A, only section 4 is scheduled on C). Thanks in advance for any advice!

mrfixit

Moderator

Posts: 1,510

Location: USA

2

Sunday, July 5th 2009, 12:46pm

Try this

If you're positive the programming is correct try this. When the C program comes on and you have two valves running at the same time, disconnect the wire from the station number 1 terminal and see if the valve shuts off. If it shuts off then the controller is telling it to run and the controller is the problem. If it stays on you have a wiring issue. If you have a wiring issue I would suspect that the dripline would come on when station number 1 on the A program starts. If you determine it's the controller you could try abandoning the number 1 terminal incorporating the number 5 terminal.