Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

joebatten

Unregistered

1

Saturday, March 27th 2010, 9:56am

low pressure in one zone

I have a two zone Toro system that has worked well for many years. Late last year zone 1 developed very low water pressure. Zone 2 works perfectly. Zone 1 does not appear to have any breaks or leaks anywhere. No changes have been made to either zone in several years. It is almost like the valve is not opening all the way. Any suggestions???

mrfixit

Moderator

Posts: 1,510

Location: USA

2

Saturday, March 27th 2010, 11:48am

Most of the time the problem you've described will be the diaphragm. Needs replacing.


Here's a good way to find out. While the valve is running open the bleeder screw. It will work without
the valve running but you can see the change in the sprinkler spray with it on. If opening the bleeder screw increases the flow then replace the diaphragm. The valve might stick open if the diaphragm is bad. Have a game plan to turn it off.
Turning down the flow control will do it. If there's no flow control tapping/light banging on the valve might close it. I use the handle of a screwdriver. Also know where the shut off valve is. Turning off the water then back on can close it.
---
Still could be a break in the system somewhere.