backflow preventer oveflowing

I had to replace the bonnet and poppet on my backflow preventer when I went to turn on my sprinkler system. However, when I turn it on with minimal water pressure, water comes up over the top of the new bonnet and poppet. I'm afraid that if I turn the water pressure higher, it will simply blow the bonnet and poppet again. Any ideas on what might be causing this? Could it be a problem with the check valve? How do you determine if the check valve needs to be repalced?

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Saturday, May 29th 2010, 9:31am

Close the valve downstream of the bonnet where the water is coming from. Now turn on the supply and open it completely.

LEH

Starting Member

3

Saturday, May 29th 2010, 4:15pm

Thanks! That worked and my sprinkler system is back online!