Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

t_shea

New Member

1

Saturday, September 18th 2010, 10:46am

Rainbird ESP-6Si controller, one zone will not come on electrically

I installed my system about 15 years ago and I have maintained it over the years. I had this problem once before, but was able to fix it by installing a new solenoid on the valve. This time however, that procedure had no effect. The zone will come on fine by turning the valve in the valve box. It just won't come on electircally via the controller.

So, I got my multimeter and tested the resistance at the controller, and all zones except that one measure 0 ohms. What does that mean and what do I do from here? Does that mean there is potentially a broken wire? Bad controller? Where do I go from here?

Thanks to anyone who can help! :rolleyes:

Central Irrigation

Supreme Member

Posts: 364

Location: Central Minnesota

2

Saturday, September 18th 2010, 2:47pm

If I understand you correctly: The zone in question OHMS out fine, but the remaining zones read 0 OHMS?



If your multimeter is showing 0 OHMS, it usually indicates a broken wire. Most likely the common.

Step 1: Check that the wire is well to connected in the controller

Step 2: OHM out the selenoid at the selonoid wires (make sure you didn't replace the old one with a bad one)

Step 3: Check the selenoid wire connections in the valve box (Probably where you'll find the problem, being that you recently disconnected these wires). Make sure you didn't accidently grab the wrong end of the zone wire. Also make sure your common wire is wired in correctly. The only selonoid that has only one common wire is the one at the end of the wire, so make sure that both ends of the common are making contact.



If you have multiple valves in a single valve box, make sure one wire from each selenoid is connected to the common.

t_shea

New Member

3

Sunday, September 19th 2010, 10:40am

Actually, just the opposite

Thanks for your reply, and I will double-check the wiring in the valve box. (only one valve per box) When I say just the opposite, I mean that all but the circuit in questions, caused the multimeter to swing from the far left to the 0 ohm location on the right, where the zone wit the problem does not move the needle on the multimeter at all.

Also, I also tried two different new solenoids, and neither worked. Which makes me think it's the wiring or the controller. I also took a working solenoid from another valve and put it in place, and it still would not work. So, it's not the solenoid. And as for the wiring, I simply cut the old solenoid wires rather than undoing the wirenuts that connect the power and common from the controller; so there's no way I have them connected wrong.

I checked the voltage at the controller & it's working (24v) when each circuit is on. However, I have no voltage reading at the valve. How can I trace the buried wire to figure out where the problem is located.

Thanks

This post has been edited 1 times, last edit by "t_shea" (Sep 19th 2010, 2:11pm)


Central Irrigation

Supreme Member

Posts: 364

Location: Central Minnesota

4

Sunday, September 19th 2010, 1:08pm

Then yes, there is a problem with the zone wire or the common for that valve. Is the valve in question at the end of the multistrand wire or is it between two other valves? A simple way to check is to look at the wire nuts for the troubled valve and see how many common wires go into the wire nut. A valve at the end of the multi strand will only have one common wire and a selonoid wire in the wire nut. A valve in the "middle" of the multistrand will have two common wires and the selenoid wire. We need to figure out if it's the common or the zone wire that is broke.



Another thing you could check is the voltage of the bad zone at the controller. Turn on that zone at the controller, and using one of the selonoids, touch one wire to the common post and the other to the zone post. You will more than likely hear the selonoid activate. I advise using the selonoid, because voltage readings don't necessarily mean you have the power to activate a selonoid. If you would like to check it with your multimeter, you should have readings of 24-26 volts.



Conversly, out at the valve box we'll use your multimeter to check the voltage of your zone wire. Undo the selonoid wire and zone wire. Stick one probe into the ground and touch the other probe to the zone wire. You should read in the neighborhood of 24-26 volts.



If you read values lower than these it is safe to assume you have a problem with your zone wire. The only way it could be a common wire problem is if the valve in question is at the end of the wire, being that all other zones show resistance.



Once you make any repairs, check your work with the selonoid.

mrfixit

Moderator

Posts: 1,510

Location: USA

5

Monday, September 20th 2010, 4:22am

I was hoping Boots would answer this question. He's the one who always recommends measuring the continuity of the wiring. A reading of 0 doesn't indicate a broken wire. It means no resistance. A broken wire would read infinity. Disconnect the ground wire from the controller. Put your meter on the lowest setting and check again. There should be a reading because of the solenoids. Should be somewhere between 20 and 60.

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

6

Monday, September 20th 2010, 1:01pm

I might have chimed in sooner, but a reading of zero ohms is, in theory, a dead short, but those aren't seen very often in sprinkler wiring, when you use digital multimeters. Modern controllers would cut themselves out when feeding a dead short, and likely display an error message.