Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

1

Saturday, June 11th 2011, 11:36am

Valves -Rainbird DV series

My system = 13 Rainbird DV valves with 3-4 of the 5000 heads on each zone.

System was installed by a professional and lines were blown out last fall by him.

Turned on this spring-ZONES 4,6,10,11,12 worked by controller no work on ZONES 1,2,3,5,7,8,9,13.

RASTER Test Ok to all zone valves.

Turned DV valves 1/4 turn CCW and some or no water comes out of head.[hear water running at valve,sprinkler heads stay down]

28 volts to valves from controller[ok] Took valves apart and everything looks good. Hooked up compressor and the heads pop up with the valves 1/4 turn ccw. I am wondering if the professional used too much pressure and damage the lines or ?
Swapping good solenoids in position of bad doesn't help manual 1/4 turn or controller electrical operation.


Help

This post has been edited 5 times, last edit by "WillRainman" (Jun 11th 2011, 6:42pm)


Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Saturday, June 11th 2011, 12:18pm

Swap solenoids between good and bad zones, and report back.

5524

Unregistered

3

Saturday, June 11th 2011, 4:48pm

Rainbird DV Valves

Swapping bad zone 1 solenoid with good zone 4 results---Zone 1 operated by zone 4 solenoid still bad. Zone 4 operated by zone 1 solenoid works. Not a solenoid problem,

4

Saturday, June 11th 2011, 7:25pm

Rainbird DV Valves

5524 was WillRainman

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

5

Saturday, June 11th 2011, 7:29pm

now you open up a faulty valve and have a look-see

6

Saturday, June 11th 2011, 10:08pm

Rainbird DV valves

Refer to original message---Took valves apart and everything looks good

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

7

Sunday, June 12th 2011, 7:49am

There could be a blockage in the body of a valve - one way this is evident, is if a valve will operate by way of the bleed screw, but not by way of the solenoid.

8

Sunday, June 12th 2011, 8:00pm

Rainbird DV valves

Bought a new valve repair kit and put in new diaphram in valve 1 and it works now.

It seems odd to have this many diaphrams bad in one year. Anyone have a sectional view of the DV valve ?

What fails in them or do they dry out?

Turned on this spring-ZONES 4,6,10,11,12 worked by controller no work on ZONES 1,2,3,5,7,8,9,13.

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

9

Sunday, June 12th 2011, 8:43pm

city water or well water?

10

Monday, June 13th 2011, 8:23pm

Rainbird DV valves

rural water system

Found a small split in the diaphram, [hard to see] Took apart valve 13 and that diaphram had a split too.[exactly same as previous] Question--blowing out the system for the winter with too much pressure cause this ? Age of system is 4 years and 8 out of 13 diaphrams bad at one time.