Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

chr4993

New Member

1

Tuesday, June 28th 2011, 12:36am

Rain Bird JTV/AS-100

Hi there. I have a JTV/AS-100 valve but have a Hunter SVC-200 controller. It will only operate a DC latching solenoid. Does anyone know if the Rain Bird TBOSPSOL solenoid will work with the JTV valve I have?



Thanks

mrfixit

Moderator

Posts: 1,510

Location: USA

2

Tuesday, June 28th 2011, 2:06pm

Yes it will. I have some RainBird valves operating in the field with the Hunter battery operated controller you've mentioned.

chr4993

New Member

3

Wednesday, July 13th 2011, 7:34pm

It works!

Yes it will. I have some RainBird valves operating in the field with the Hunter battery operated controller you've mentioned.
Thanks for the reply. I bought the DC latching solenoid mentioned above and tested it with the valve mentioned above and it works great! NOTE; Rain Bird tech support said it would not work.