Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

1

Wednesday, May 16th 2012, 9:18pm

Spring setup - Febco (765?) beast gives me alot of water hammer and other stress!

Every spring when I open the valve to restart the irrigation system after it was wintereized, I have to open it partially and wait a while before opening it further because severe water hammer develops and it sounds like something is going to break! I close the valve (looks like 3/4" or 1" line, by the way) until the water hammer stops, then try opening it a little again and repeat. I stay nearby the shutoff valve until I am sure the banging will not resume.

Usually after a matter of minutes, the underground plumbing is filled and the water flow and noise stop. There is a water meter in the basement below the valve with a rotating vane and I can see it slow down...eventually.

My question is about how long it should take and how to tell if there is a problem. Last year the Febco device wouldn't stop leaking and I bought a replacement parts kit (poppet and whatever). There is typically some water flowing onto the ground outside but it normally stops when the system is 'full'.

It always seems to take a disturbingly long time to 'fill' the system. I recall always feeling like something must be wrong due to how long it takes. (only 4 stations and maybe 1/6 acre yard at most).

Last night I decided the water flow was not slowing down at all and I couldn't get rid of the hammering for very long. I ended up closing the shutoff valve and postponing the startup.

How long is reasonable and what is actually normal? In my mind I think that what normally happens is pressure must build up or decrease once all the lines are filled, and the Febco device then closes - maybe it's like a check valve or similar.

Thanks for reading this far, and for any advice.

Murray
Holland MI

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Thursday, May 17th 2012, 7:00am

the Febco PVB has nothing to do your issues, but is merely displaying the results of the widely fluctuating pressure as the system fills with water. You are always better off closing the outlet valve of the PVB before opening the system supply valve. Then you can open (slowly) the PVB outlet valve and the system will fill without water escaping the PVB. Pipes will still bump and bang, but that is air in the zone valves.

3

Saturday, May 19th 2012, 10:08am

OK, thanks Mr. Boots.

Before reading your response I went out & looked (during the day, this time) at the 765-1 and out of curiosity shut off the output valve between the 765-1 and the underground pipes to see what would happen. I had the supply valve open just enough to have some flow but no hammer. After closing the out put valve, the water leaking out of the top of the 765-1 stopped after several seconds. I decided this probably indicated the 765-1 was working properly (shutting off with back pressure) but wasn't very significant because I still obviously needed the output valve open.

The water's been running, at reduced flow to avoid hammering, probably 20 minutes now...that just seems too long to me. I'll go shut off the output valve & see how things act.

Thanks

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

4

Saturday, May 19th 2012, 5:51pm

Different systems will or won't have turn-on issues as zone valves fill with water. Yours is marginal, and you want to fully close the PVB outlet valve before you fully open the supply valve. Having done that, you slowly open the PVB outlet valve, and job done.