I have a Rain Jet classic RJ711 valve system. When the conroller automatically activates the system the sprinklers do not rise and the water flow is confined to the edges of the sprinklers. When either the solenoid or bleed screw is turned counter clockwise as directed I get an excellent spray. What is the problem and how do I fix it?
I have the same issue.. the issue is resolved by removing the white plastic retaining collar on the solenoid that is in place to retain the plunger and prevent it from falling out during shipping and handling. It needs to be removed before installation of the solenoid onto the valve body. Valve works great w/ the plastic collar removed.
I'm not so sure the RJ711 solenoid has the white retaining collar. I believe the valve was redesigned into the 2711 before the collar was added to the solenoid.
If you know otherwise I'd be happy to hear it.