Irritrol Slim Dial Troubleshooting
I have an Irritrol Slim Dial that suddenly won't turn on any zones. I have tried to summarize the steps I have taken below.
1. Reset controller by removing power and battery from the Irritrol Slim Dial controller. (Followed steps per the user guide/manual.)
2. Confirmed the water valve is open. I can manually open the valves and get sprinklers to come on.
3. Measured voltage across the wire terminals at the controller is ~26V from comm terminal to each respective zone terminal.
4. Voltage at the solenoids is <0.02 V, even when the zone is "energized" by the controller.
Shouldn't the voltage at the solenoid from comm to valve wire be ~26V when the respective zone is energized?
Should the voltage across the terminals at the controller always be ~26V? Or should the voltage only be ~26V when the zone is energized?
Other steps or recommendations for troubleshooting are greatly appreciated.
Thank you in advance.