You are not logged in.

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

smoore

New Member

1

Tuesday, July 17th 2012, 10:05am

to much resistance in zone 2

We are having some issues with our sprinkler system and we aren't sure which way to go. Some of our zones shut down early and others only stay on for two minutes. We have traced the problem to wiring in zone 2. When we test the continuity with a multimeter all of our zones check out fine, but zone 2. It has a much higher resistance reading. I know that this means that the wiring has an issue. Is this where I start to dig up my yard? And is it possible that this is causing the other zones to not work properly or did this wiring issue also damage my timer and should it be replaced?

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Tuesday, July 17th 2012, 10:36am

If you take current measurements for each zone, while they are running, you may find some intermittent faults.

Rate this thread