You are not logged in.

prich01

Unregistered

11

Monday, August 27th 2012, 6:40pm

Well, the construction guys that hit the pipe frantically messed with stuff to try and turn water off until I could get there to do so. In the process they opened the drain valve without ever telling me. That was the "leak". Now though I have an issue with my first zone wanting to stay on constantly as long as water is on. Even with control box off. I'm starting to wonder if this well ever end haha. Seems to go from one problem to another. Any ideas?

mrfixit

Moderator

Posts: 1,510

Location: USA

12

Monday, August 27th 2012, 8:33pm

Could be debris in the valve from the pipe repair.
Does it shut off if you disconnect the wire?
Make sure the solenoid is snug.
Check the diaphragm while you're at it.

Rate this thread