Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 5332 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 2 posts

Monday, September 21st 2009, 1:07pm

by HooKooDooKu

YOU CAN NOT USE AN ANTI-SIPHON VALUE BEFORE A VALVE MANIFOLD. Anti-siphon valves are ONLY designed to be used at the valves in in manifold. When you use it as a master valve before the manifold, the valve might work, but the "Anti-siphon" component will NOT provide ANY anti-siphon protection.

If you do not want to use anti-siphon valves for the manifold, then you need to use a PVB (Pressure Vaccum Breaker) Back Flow Preventer between the water source and the valves such as this:
http://www.sprinklerwarehouse.com/Wilkins-WK720A-100-PVB-Assemby-p/wk720a-100.htm

Monday, September 21st 2009, 12:04pm

by bulfo3

anti-siphon valve in a box?

We're new at this, and I have a quick question. We're putting in a small, home sprinkler system, and we have a manifold with 3 valves (1 zone for grass, 2 for gardens), and a box that's big enough for them to comfortably go in. We have the anti-siphon valve to go between the house line, and the manifold, but does it have to be in the same box as the manifold, or in a box at all? Our yard is really flat, so having it 6 inches above the sprinkler heads isn't hard. Is putting a box over the anti-siphon valve just to keep it from getting bumped or exposed to the elements / kids? We'll drain it when it's winter (blow out the lines with an air compressor).

Thanks,
Tom in NM