Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 3881 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 10 posts

Tuesday, September 10th 2013, 7:03pm

by Don747 (Guest)

RE: You saved me $250

Worked for me, too.

Thank you...

I found your thread after googling my pipe thumping. I had the same exact problem which started after I finished the basement. I had a plummer state he would place a special valve outside my house with the sprinkler that would have to be removed every winter that SHOULD fix the problem. (Total price of $250)
After reading your fix, I remembered that the whole house valve was not completely opened when I first shut off the water to plumb the basement. When I finished plumbing, I completely opened the valve as I had always been taught.
After reading this, I turned down the main water supply and also solved the problem.
Thanks SOOO much!. :D :P :thumbsup:

Friday, May 25th 2012, 2:22pm

by GatorGuy

Glad we could help.
Have a good weekend.

Friday, May 25th 2012, 2:12pm

by jhpkmr (Guest)

You saved me $250

I found your thread after googling my pipe thumping. I had the same exact problem which started after I finished the basement. I had a plummer state he would place a special valve outside my house with the sprinkler that would have to be removed every winter that SHOULD fix the problem. (Total price of $250)
After reading your fix, I remembered that the whole house valve was not completely opened when I first shut off the water to plumb the basement. When I finished plumbing, I completely opened the valve as I had always been taught.
After reading this, I turned down the main water supply and also solved the problem.
Thanks SOOO much!. :D :P :thumbsup:

Wednesday, August 4th 2010, 8:00pm

by SNG

I believe I have fixed the problem. :D



And the solution could not have been simpler. I started thinking that this all started happening a year and a half ago, when our PRV stopped working, and I had a plumber replace it. Today I put a gauge on our hose bib, and saw that the house pressure was 80 psi (Only a little lower than the incoming 90-100). I think he adjusted it so that we'd have a lot of house pressure without it being so high as to cause water hammer. I got thinking about the theory that the fast water/instantaneous low pressure in the starting-up sprinkler line was drawing water from both sides of the tee, so I adjusted the PRV so that the house pressure is 60 psi.



I then tested the sprinklers. No more thumping. I can't believe it was such an easy fix.



Thanks for your help - trying to troubleshoot this one was not fun....

Wednesday, August 4th 2010, 8:20am

by Wet_Boots

The ever-so-slight problem with that page is that it suggests placing a check valve in the house supply without first installing an expansion tank on the water heater. If you do install such a check valve, and there is no expansion tank, the water heater will do its job of heating water, and since heated water expands, the increased pressure can burst the plumbing.

-

By the way, if you think about it, every home with an expansion tank in their plumbing, and no check valves, might be a likely candidate to create pipe banging when a sprinkler zone turns on. And yet, this isn't happening, and why? Because a properly designed sprinkler system doesn't have excess flows that create the pipe-banging problems.

Tuesday, August 3rd 2010, 11:14pm

by hi.todd

Yeah you are probably right.
It sounds like a good idea.

Good Luck :thumbsup: :thumbsup:

Tuesday, August 3rd 2010, 10:37pm

by SNG

I found another possible solution online - What do you all think of this idea?



http://www.rilawnsprinklers.com/blog/2009/07/noisy-pipes-when-irrigation-system-is.html



It seems to describe exactly what I'm experiencing. (The paragraph on "System is making a loud noise when the zones are starting, then the noise goes away until the next station/zone starts or only on specific zones.")

Tuesday, August 3rd 2010, 9:11pm

by hi.todd

You said that the diaphrams did not fix the problem. What is the valve make and model that you changed the diaphragms? How many diaphragms did you change? Is there a Master Valve you can tell this by the controller? What is the model of the Rotor Heads you are using and what is the nozzle in there? Rotor heads will use more water or Gallons per minute the higher the water pressure. If you have High water pressure and you nozzles would use 2 gallons per minute with 50 PSI they will use 6 gallons per minute at 80 PSI. This is just an example, but you get the idea. If you are exceeding the recommended flow through your pipe size you will get the water hammer. 1 inch pipe should only flow 15 or so gallons off of the top of my head. 3/4 pipe should flow up to 10 gallons per minute off the top of my head. 1/2 inch pioe should flow 5 gallons per minute off the top of my head. Also you don't want the water in the pipe to flow faster than 5 feet per second. This is why the pressure and nozzle selection is so important in how many gallons per minute is flowing through your pipes. The cheapest way to fix it is to buy new rotor heads and use the nozzle that has a chart that can tell you how many gallons per minute are flowing with your high pressure and stay with in you pipe size flow chart recommended flow as I have outlined above. The next is to use flow control valves. You probably need new heads anyway. Unless this all started when you changed the heads or paid somebody to change the heads that did not know what they were doing.

Good Luck :thumbsup: :thumbsup: :thumbsup:

Tuesday, August 3rd 2010, 6:53pm

by Wet_Boots

Flow control valves are a good idea, since they can be throttled down, and that will slow a rush of water. Unfortunately, this isn't an easy problem to deal with, especially since it is mostly the result of poor system design.

Tuesday, August 3rd 2010, 10:57am

by SNG

Well, there's already a 3/4 inch copper supply line - I'm hesitant to go replacing that unless it's a surefire solution.



What do you think about replacing the valves with ones that have flow control? I've also seen pressure regulators that can be installed on the valves. In your opinion, is it more of an issue of high pressure, or high velocity?