You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 6046 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 5 posts

Sunday, October 14th 2007, 10:00am

by Wet_Boots

One could still get a full voltage reading at the valve box with faulty wiring. Current and resistance measuring takes longer, but reveals more.

Saturday, October 13th 2007, 3:18pm

by nestors

1st check voltage at each valve,if you have 27 volts then your selenoid is bad,if not then you have a bad wire to valve.

VINCE.........

Friday, September 21st 2007, 9:55pm

by Bill Painter

Sometimes electrical nuances are tricky. When you test the resistance to the valves from the clock as Wet Boots suggested, be sure it's 20 Ohms or more on each valve solenoid. Different solenoids (brands) have different resistances. Most are 24-25, 45 more or less, and Toro is generally 55 Ohms per.... Wire lengths can add an Ohm or two depending on distance from the clock.
Check continuity across from 1 to 2, 1 to 3, 1 to 4 and so on. Each should read twice what the common to valve resistance is. This would tell you the HOT connectons to the valves are OK or not. If they are all in the same ballpark, I would seriously consider re-doing ALL OF THE COMMON CONNECTIONS in the circuitry.
One last thing... when testing the solenoids and valves, defeat the rain sensor by jumping the terminals.. it might be shot.

Friday, September 21st 2007, 1:30pm

by Wet_Boots

Do resistance testing on the wiring. Are you connecting your multimeter to the solenoid wires out in the field?

Friday, September 21st 2007, 10:37am

by Kevinrmac

Controller not turning the valves on...

The system stopped operating last month. We rechecked the one location where we had dug recently, and confirmed that the control wire was not damaged. We haven't had any unsually electrical activity, and the controller appears to be working correctly. We did pull the power and battery, and reprogrammed it just to be sure.

General info that I do know.
Controller: Rainbird ESP 8SI
Municiple water supply. I can manually operate the valves and each zone works.

Using a multimeter, Each zone reads 27 volts at the controller contacts when the controller turns them on. They read between 24.5 and 26 volts at each of the valves when activiated.

Would I get a good voltage reading at the valve if the common line was broken somewhere?

I removed the rain sensor for testing to make sure it wasn't somehow causing a problem.

I can't imagine that all 8 solenoids crapped out at the same time. Any suggestions would be greatly appreciated. Thanks.

-Kevin