You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 7290 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 4 posts

Monday, June 7th 2004, 5:43am

by HooKooDooKu

I would put a hose bib vacuum breaker on the new hose bib because once you attach a hose, you could wind up with the end of the hose higher than the PVB.

Monday, June 7th 2004, 5:18am

by bgeddes

Thanks Aquamatic.

> Minimum of 12" below the PVB

If I installed hose bib vacuum breakers, would I still need to be 12" below the PVB?

I will be installing my system in about 3 weeks.
(The SprinklerWarehouse boxes have arrived [:)])

Due to my sloped lot, I'm running the mainline uphill to connect to the PVB. Two of these hose bibs would be installed at the highest elevation.

I'm starting to re-think the PVB decision.
My first thought was to install a double-check assembly to avoid the 12" requirement. But after reading the (hazard) controversy surrounding DCs, I decided on a PVB. My life would certainly be easier with a DC. An (expensive) RPZ would reduce too much pressure.

Monday, June 7th 2004, 4:22am

by aquamatic

Just blow it out as you would your zones then leave it open for the winter. You do need to install those just like sprinkler heads a minimum of 12" below the PVB.


Friday, June 4th 2004, 6:40pm

by bgeddes

Additional hose bibs connected to mainline

I would like to add some additional hose bibs away from the house.
The hose bibs would connect to a vertical pipe 2-4 feet above ground.
The vertical pipe will connect to the 1" PVC mainline.
All bibs will be downstream of the PVB.

Should the vertical pipe be copper or galvanized steel?
Could the vertical pipe be (wrapped) PVC and enclosed in a housing/box?

Will the vertical pipe need support other than a ground stake?

Are there winterization issues I should be concerned with?
(bib freeze, irrigation blowout, etc.)