Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 6399 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 2 posts

Friday, October 20th 2006, 9:22am

by HooKooDooKu

Just like control valve, DC have a pressure loss associated with them, but they will usually be much less than RPZ.

For example, if you compare Watts RPZ (009), both the 3/4" and 1" have about 12-15psi pressure loss. But the Watts DC (007) in 3/4" has only about 5psi loss while the 1" has about 3psi loss.

Friday, October 20th 2006, 7:45am

by GSH

DC Pressure Drop

I am aware that RPZ anti-syphon valves have a pressure drop. Is this also true of the DC type? If so how much?