Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

1

Saturday, November 1st 2014, 10:37pm

Water gushes out from the anti-siphon cap and then stops

I installed five Rain Bird anti siphon valves about 20" higher than the highest sprinkler head. They share the same supply line and shutoff valve. The water pressure is 80 psi. I know it's too high.

Four of the five valves work perfectly. After turning off the valve, water gushes out from the anti-siphon cap of the fifth valve for a few seconds and then stops.

I want the valve to operate completely dry. I would appreciate it very much if you could tell me what I should to make the fifth valve work like the other four valves.

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Sunday, November 2nd 2014, 8:32am

There really isn't anything practical that you can do about that water, as it comes from the spring-loaded sprinkler heads pushing some water backwards, while the heads retract. Different sprinkler heads would have to be installed. Or maybe only one different head, just so that at least one head would gush water around the 'wiper seal' during retraction.

In olden days, all spring-loaded heads would gush water as they popped down, because the seals were simpler than they are today.

3

Sunday, November 2nd 2014, 10:25am

Thank you very much your inputs. The fifth zone do have two spring-loaded sprinkler heads. But zone 1-4 also have spring-loaded sprinkler heads. Any idea why water gushes out only from the anti-siphon cap of the fifth valve?

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

4

Sunday, November 2nd 2014, 12:11pm

Not from the information you provided. In any event, this 'flow-back' has been known about for decades, and the anti-syphon valves are still code-approved.

5

Sunday, November 2nd 2014, 7:37pm

You are absolutely right! After I replaced the two spring-loaded sprinkler heads with regular heads in zone 5, no water gushes out from the anti-siphon cap of the fifth valve any more. Now water gushes out from the anti-siphon cap of the 3rd valve because there are two spring-loaded sprinkler heads in zone 3. I will replace them with regular heads tomorrow.

There are no spring-loaded sprinkler heads in zone 1 and 2. There are spring-loaded sprinkler heads in zone 4. But they are located downhill. So I don't expect the same problem in that zone.

Thank you very much for your help!

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

6

Monday, November 3rd 2014, 8:05am

You might complete the experiment by switching back one head, and see what results. This isn't strictly about the spring-loading, but about whether the heads can gush water when they are not completely popped up. (sometimes called "flow-by")

7

Tuesday, November 4th 2014, 6:39pm

strange thing happened. After I replaced the two spring-loaded sprinkler heads with regular heads in zone 3, water not only gushes out from the anti-siphon cap of the 3rd valve, but also from the 5th valve again. Any ideas?

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

8

Tuesday, November 4th 2014, 8:27pm

How many hundreds of dollars are you willing to spend to make this go away?

9

Wednesday, November 5th 2014, 1:29am

Do inline sprinkler valves have the same problem?

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

10

Wednesday, November 5th 2014, 4:51am

They do not. That's where the hundreds come in. Install a Pressure Vacuum Breaker, along with underground valves, and no water exits anything but the sprinkler heads.