Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

tviles

New Member

Posts: 13

Location: USA

1

Friday, October 13th 2006, 7:16am

Foot Valve Sizing

Will be running a 2 inch pvc pipe to creek for intake to pump, I will need a foot valve. Question is: I can find 1½ valves no problem, will that work? Pump intake is 2", 1½ hp electric motor. Approx. 30 gpm pump. Do I need to install a tee and put on two 1½ foot valves? Most of my zones are only 2 to 3 rotors per zone. Pump will be 15 to 20 feet from creek side. Thanks, Tracy Spring Hill, KS

Wet_Boots

Supreme Member

Posts: 4,102

Location: Metro NYC

2

Friday, October 13th 2006, 10:20am

It doesn't have to be a foot valve. Combine a 2-inch check with some sort of inlet screen. Myself, I would have the check at the pump, and just screen the intake, unless the vertical suction lift is over, say, ten or fifteen feet.

tviles

New Member

Posts: 13

Location: USA

3

Friday, October 13th 2006, 4:49pm

Thanks WB you always offer a different approach. I think I will go with what you suggested for the initial test.