Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

philly56

New Member

1

Wednesday, April 11th 2012, 12:55pm

Flow rate

I have a 3 inch water meter with a 3 inch service line (type k copper) that runs into the building for about 30 ft. It then reduces down to 1.5" copper for 10 ft. They then tee'd off with 1" copper for 20 ft. The 1" is what is being used for the supply to the POC for design. I would assume that I use the flow rate of 1" copper at 7.5"/sec. roughly around 15 gpm. Would this be correct?

2

Wednesday, April 11th 2012, 4:19pm

Using the Hunter tech handbook it looks like you'll be fine. They indicate closer to 16 but 15 would be a safer bet.

philly56

New Member

3

Wednesday, April 11th 2012, 4:38pm

Thank you.