You are not logged in.

Reply

Dear visitor, welcome to SPRINKLER TALK FORUM - You Got Questions, We've Got Answers. If this is your first visit here, please read the Help. It explains how this page works. You must be registered before you can use all the page's features. Please use the registration form, to register here or read more information about the registration process. If you are already registered, please login here.

Attention: The last reply to this post was 3567 days ago. The thread may already be out of date. Please consider creating a new thread.

Message information
Message
Settings
Automatically converts internet addresses into links by adding [url] and [/url] around them.
Smiley code in your message such as :) is automatically displayed as image.
You can use BBCode to format your message, if this option is enabled.
Security measure

Please enter the letters that are shown in the picture below (without spaces, and upper or lower case can be used).

The last 10 posts

Tuesday, July 22nd 2014, 7:17am

by Wet_Boots

Very strange you reported that the hammering was still occurring after you supposedly followed the suggestion to operate the system without using the controller.

Monday, July 21st 2014, 9:14pm

by JumPinJimMie

update

The problem has been found. I changed out the wiring from the contr4ol box to the valves. While I was removing the old wire ( it ran up from my basement between the rafters to outside), we found a spot on the wire where it had rubbed through and was intermittently contacting the staple. Once the new wire was put in the problem stopped. We think the short was causing the valve to open and close randomly.

Friday, July 18th 2014, 9:20pm

by Wet_Boots

Check for partially closed valves in the water supply chain. Forget the controller for now, since it was removed from the suspect list when you operated zones without it.

Note that a jammed check valve in a backflow preventer might also be a flow restriction, which is what you're looking for.

Friday, July 18th 2014, 4:10pm

by JumPinJimMie

update

Ok, I opened the zones manually, by turning the bleed screw open, and almost every zone would hammer. How do I check the voltage for 24v from the transformer?
There are 8 zones and the majority have 4 rotors with 1.5 gpm nozzles. I have one zone that is for the flower beds and its using 8 pop up sprayer (not rotors).
I'm going to attach pictures of the system. Also have called my irrigation district to have them come check my pressure, flow rate, and back flow.
Ive changed everything but the control box, which is a Rachael (Turf products Division) 508PR
The hammer is so loud it shakes my floors and makes my dog go nuts. I noticed no water is flowing through the city main valve when this is happening.

Another note: Ive registered for this site, but can't complete registration. It never sends me the email with activation code. Ive tried other emails with same result. This needs to be fixed for pictures, I think.
Thanks

Wednesday, July 16th 2014, 5:15pm

by Wet_Boots

Check that there aren't any purely mechanical issues by manually opening a zone(s), without use of the controller.

Wednesday, July 16th 2014, 4:44pm

by irrigirl (Guest)

Water Hammer

Are you running from a pump? And how many sprinklers on each valve?
Is it hammer or could it be air in the pipes? Maybe the following link can help you with that.
http://www.sprinklerwarehouse.com/DIY-Fixing-Water-Hammer-and-Air-in-Pipes-s/7086.htm

Wednesday, July 16th 2014, 4:35pm

by irrigirl (Guest)

Water Hammer

Are you running from a pump? And how many sprinklers on each valve?
http://www.sprinklerwarehouse.com/DIY-Fixing-Water-Hammer-and-Air-in-Pipes-s/7086.htm

Wednesday, July 16th 2014, 12:21am

by JumPinJimMie

Update

Yes, its using a control box.
Ok, I tried reducing the amount of water used for each zone by changing out all the rotor sprayers with Rainbird professionals 5000 using a 1.5 gpm nozzle (down from the standard 3 gpm). We then cut out the 8 valve manifold and built our own. We used rain bird valves. When removing the old manifold we found on the end of the "T", buried in the dirt, a little drain with screen. I was surprised because looking more closely at this, it looks like a really small check valve (small little spring inside). Which allows the manifold to drain when there's no water pressure. After doing all this work, were still getting really bad water hammer. I can't tell you how frustrating this is. I built our new manifold the same as the old one and reused the little drain check valve. Do you think this could the reason for all the water hammer?
Tomorrow, I'm going to check the output power from the controller as suggested. Thanks for your help.

Tuesday, July 15th 2014, 3:51pm

by irrigirl (Guest)

Troubleshooting

Chattering solenoids are usually a power issue.
Do your valves open with the timer? Are you getting 24v from your transformer?
Also does sound like a water hammer issue of some sort. I wonder if a loss of power would cause this.

Sunday, July 13th 2014, 4:35am

by mrfixit

I ran across your scenario just last week. It was a new problem which just appeared over night.
It turned out the RainDial controller was sending out a pulsing signal to the solenoid. It would open close open close open close open close causing wicked hammering inside the house which was a good 50 feet away.
I've only seen this three time in 20 years. Two of the controllers were RainDials. The other I can't remember.

Of course there are many causes for water hammer. I'm just giving you one possibility.