None of the water will have to go more than 165' past the valve.If I am reading the chart correctly, I should have @ 9 psi loss at 9 fps velocity with 1" pipe. Am I doing this right? Do I have to add up all of the pipe going to all 7 of the heads?
9 fps is WAY into the "DANGER" zone. If you'll notice, the chart shadows everything where the water speed is exceeding about 5 fps. Remember, kenetic energy quatruples as speed doubles.
Additionally, a 9psi loss in a system that was designed for less than a 5psi can still affect performance. By how much? Can't say because we don't know how concervitive the design was. Too little pressure will result in heads not throwing the water as far as it's supposed to. An extra 5psi pressure drop may or may not make or break, the design.
As for how to add things up right... here's what you have to do. You start by determining what the gpm is EXPECTED to be at each head. Then you have to account for that much gpm from the valves to the head. So if a pipe is supplying two heads, each expected to output 2gpm, then before the pipe splits to the two head, you have to account for 4gpm flowing in the pipe before the split and 2gpm in each pipe before the split. For pipes that lead to three heads, you have to account for the gpm flowing to all three heads, etc. So once you know the expected gpm of each pipe segment and the approximate length of each pipe segment, you can calculate the psi losses in each segment. You then determine if the point the fartest out will still have enough pressure (after you account for all the pressure losses through the valves and before the valves) at the head to see if it will perform within spec.
For more information, try checking things out starting at this page:
http://www.irrigationtutorials.com/sprinkler01.htm